    I replaced a shorted out well pump control & capacitor & the breaker stillkicks off
    I want to know why the breaker kicks off after I replaced a shorted out well pump controler & a capacitor
  • Aug 18, 2012, 11:19 AM
    hkstroud
    Assuming that this is a submersible pump, the short could be any where. Could be in line to well head, could be in line down the well or could be pump.

    Provide more information please.
  • Aug 18, 2012, 03:33 PM
    rwalker04
    Quote:

    Originally Posted by hkstroud View Post
    Assuming that this is a submersible pump, the short could be any where. Could be in line to well head, could be in line down the well or could be pump.

    Provide more information please.

    Thanks Harold That's not the answer I want , but I think you may be right . Thanks A Bunch for youur help. rwalker04
  • Aug 18, 2012, 04:27 PM
    hkstroud
    Suggest that you disconnect the line at the well head. Cap the wires and turn breaker on. If breaker trips, fault is in the line to the well head. If it doesn't it is either in the line down the well or the pump.