    Splicing the EGC with feeder cables
    The equipment grounding conductor ran with feeders from sub-panel to sub-panel, can this or should this EGC be spliced at pull boxes?
  • Aug 19, 2012, 04:28 AM
    tkrussell
    Of course the equipment grounding conductor needs to be spliced at every junction box. Otherwise, what good is it?