    Can you strenthen a load bearing wall to run piping through it?
    Can you strenthen a load bearing wall to run piping threw it?
  • Aug 13, 2012, 07:54 PM
    ma0641
    How big is the pipe and the wall you want to go through? You may not have to do anything.
  • Aug 13, 2012, 08:21 PM
    creahands
    also need to know the size of studs, 2x4 or 2x6.

    Chuck
  • Aug 14, 2012, 05:54 AM
    speedball1
    What do you want to run through the wall? Water pipes? 2" drainage? a 3" stack?
    Just how wide is this wall anyhow? Are you going through it vertically or horizontally?
    Can you tell us what you're attempting to do? Back to you, Tom
  • Aug 16, 2012, 05:15 PM
    jriemer
    Sorry about the lack of information. It is a 2x4 wall, I will be running a 1.5 inch drain line horizontally. I need to go threw three studs. Building a 2x6 wall in front of the load bearing wall is not an oppition.

    Thanks for the help!

    Jim
  • Aug 16, 2012, 05:32 PM
    creahands
    U can install a double 2x6 header to the next studs on each side with jack studs to support the header.

    Be sure to protect the pipe with steel nail plates on each side of 2x4. This will keep u from putting nail or screw in by mistake.

    Chuck