  • Mar 5, 2007, 02:09 PM
    bzitser
    Electrical specification.
    Can 20 Amp. Ciruit Breaker Support 1 Hp 115 Volt Single Phase Motor?
  • Mar 5, 2007, 02:26 PM
    Robair
    Yes It can... However, The breaker is overrated for the application.
    So look at the specs on the motor carefully... But by and large you should have a 15Amp breaker.
    It's suppose to trip when under heavy load to protect you. If you use a 20 A unit... the motor and wires can overheat and created unspeakable damage.
    Get a 15Amp breaker.
    Good luck;)
  • Mar 5, 2007, 09:42 PM
    bzitser
    Bzitser
    Quote:

    Originally Posted by bzitser
    Can 20 Amp. Ciruit Breaker Support 1 Hp 115 Volt Single Phase Motor?

    Thank's Robair for your respond, but to my knowledge I have to size single phaze breaker minimum 20% above that total amperage draw by motor and 1HP whisperflo swimming pool pump(what I want to install) has full load 14,8 amps.
    If I am right, my qwestion still stay .Please respond.
    Sinserely yours
    bzitser.
  • Mar 6, 2007, 02:57 PM
    tkrussell
    Almost correct, a 1 HP motor 1 Phase motor branch circuit and short circuit protection needs to be rated 125% of the value listed in NEC Table 430.148, which for 115 volts is 16 amps, so minimum size rating of a breaker is 20 amps.

    An inverse time circuit breaker can be sized up to 250 % of the rating in Table 430.148, depending on several other factors that may not apply, since this is only a water pump.

    Overload protection, if needed, will only use the nameplate rating of 14.8 amps, and again may or may not be required depending on other factors.
  • Mar 8, 2007, 08:21 AM
    ColGrayBeard
    Yes.

    A 1 HP motor draws about 13A at 120VAC. You should make sure that your wiring will support this load as well. Although # 14 would support 13A, the start-up current will be higher than 13A. You should wire to the motor with # 12 wire.
  • Mar 8, 2007, 08:39 AM
    ColGrayBeard
    Yes.

    A 1 HP motor draws about 13A at 120VAC. A 20A branch circuit breaker would be appropriate. You should make sure that your wiring will support this load as well. Although # 14 would support 13A, the start-up current will be higher than 13A. You should wire to the motor with # 12 wire.

    I just saw the information about the 14.7A nameplate rating. The same answer applies with the slightly higher rating.

    Based on my experience, using a 15A circuit breaker will result in a significant number of nuisance trips. The motor should have internal thermal protection to protect from overloads.