  • Aug 2, 2012, 11:02 PM
    ayyaz_hashmi
    Out Door Trip for 3 minutes & restart after 5 Minutes
    I have purchase Gree Ac 1.5 Ton
    Its cooling very nice but after 40 to 45 minutes, out door trip, Fan & Compressor stop for 3mins & after 5 minutes its restart again and after few minutes same thing will happened
    Is there any problem or its standard routien running?
    Please guide me
  • Aug 4, 2012, 11:35 AM
    thermalmedics
    Maybe contactor coil is heating up and dropping voltage out, thus the plunger pops off and the unit shuts down.

    Or

    You could have a pressure switch that is tripping. Prob a hi pressure switch that signals the refrigerant is under too much.. pressure and it cuts out to save any damage.

    Is the condenser coil clean?