What is the number of the Trane XE1100 start capacitor?
![]() |
What is the number of the Trane XE1100 start capacitor?
Trane XE1100 Start capacitor
mandour mandour is offline (1 Posts) Asked Today, 07:23 PM — 5 Views IP Edit Report
What is the number of the Trane XE1100 start capacitor?
You will find the exact value on the capacitor itself.
http://www.google.com/imgres?imgurl=...BMAM&dur=22271Make sure the replacement cap is within 5% of the original. If you have a potential relay with a start capacitor you MUST replace both the capacitor and the relay. A potential relay is square with wires at 5, 2, and 1. 5 goes to common, 2 to start, and 1 from capacitor. There is a high resistance coil between 5 and 2 that opens the contacts between 1 and 2 when the motor is spinning fast enough. You must match these relays exactly and if coil burns out relay stays in until something blows. That's why you don't risk reusing one.http://www.globalindustrial.com/p/el...FROd7Qod20kAJAhttp://www.google.com/imgres?imgurl=http://neilorme.com/pics/potential.relay.ladder.jpg&imgrefurl=http://neilorme.com/csr_motor.shtml&h=725&w=800&sz=38&tbnid=l6EikUUyYV KQUM:&tbnh=90&tbnw=99&zoom=1&usg=__11GkUjHSo4TvIxI-RfJRE9jH-ic=&docid=hSKrI--obhuusM&sa=X&ei=y8IbUKqwKYe16gG6pYH4DA&ved=0CJ4BEP UBMAQ&dur=5725