How to increase water flow when multiple fixtures running?
Dear Ask Me, I want to increase water flow when multiple fixtures are running. We have a 2900 sq foot two level L-shaped rancher built in 1963 in Atlanta. For our family of four, the water pressure is fine. When someone is taking a shower there is a noticeable drop in pressure and volume when another fixture is opened. We frequently host house guests and are unable to run two showers and another fixture, e.g. the washer machine, at the same time. The supply from the street is about 100 foot via non-copper, grey metal pipe. The OD is about 1". This comes inside and connects to 3/4" copper, passes through new PRV and new expansion tank with new ball valve main shut off. Main runs are 3/4" copper. The showers are out about 70 and 100 feet off of 3/4" copper. When I hook up a pressure valve to an outside hose spigot (1/2" line 5 feet off 3/4' line) it reads 60 psi. When I open one tub full, it drops 20 and reads 40 psi. When I open two tubs it drops 40 and reads 20 psi. When I open just one shower, the way we like it (tub near full open, but when shower engaged, the flow is cut quite a bit but with good pressure and volume), the presure drops 10 to 50 psi. When I run two showers, pressure drops 20 to 40 psi (this is not quite enough pressure and volume coming out of the shower). If another fixture is turned on, the pressure drops below 40, and pressure seems inadequate all around. If I turn the PRV up to 75, curiously the drops increase and the final pressure readings are the same as if I had the PRV regulated to 60 psi. So, turning up the PRV to 75 does not solve the problem (also at 75, the pipes rattle when I turn off the water to the shower--no problem at 60 psi). I did not try to turn the PRV above 75 psi but there was substantial thread remaining to try to do so. The valve at the street (city water) is fully open and sits at an altitude of 800 feet above sea level, although I do not know the drop or climb to our house--we sit at a relative high point compared within the neighborhood). There is no movement of the street needle when all house fixtures are off (ie no external leak). The main ball valve is new and fully open. I did not think copper corrods. I have old shower heads, but they seem to deliver good volume and pressure when run alone. If I can get this pressure issue addressed, so I can run multiple fixtures with adequate volume and pressure for when I have guests, I will address the hot water part of the equation with two 185K BTU tankless water heaters (there is a convenient "T" in our "L"-shaped house which separates three showers/baths and sinks from the kitchen, dishwasher, and washer machine). We do not have an irrigation system (and will not be getting one). What are your thoughts? Thanks, Michael
How to increase water flow when multiple fixtures running?
Good morning Michael and Happy New Year,
Has your water pressure ever been satisfactory or has this been a ongoing problem from the start?
Your local, State and National Plumbing Codes address this problem when they mandate no more then three fixtures tied on a 1/2" branch off a 3/4" main.
I think Labman put his finger directly on the cause of your problem when he zeroed in on the galvanized pipe house supply from the street.
I have seen 3/4" galvanized pipe choked down to a opening the size of a lead pencil by mineral build up over the years.
You simply don't have the volume to support running multiple fixtures at the same time.
Replace the feed from the meter with 3/4" PVC and I think your problem will be solved. Regards, Tom
How to increase water flow when multiple fixtures running?
Hi Michael,
As Labman sez, 1" Pvc is overkill. You will have more volume with 1" but I question if you'll need it. Hey! Your choice!
In my area and on the West coast of Florida we run the house supply in 3/4" schedule 40 PVC. We use 1" on multi-condos and commercial jobs.
3/4" is easier to work with and it will make a long bend without fittings if you need to line it up with the house connection. Schedual 40 PVC is rigid and comes in 20' lengths. There is a built in coupling on one end for ease of installing. Your depth should be the same as your old line To turn off the meter the city uses a "street key" call the city to shut off the meter. Once they loosen it up, a large crescent wrench with a screwdriver for leverage should be able to turn it back on. Don't forget to prime both coupling and pipe with PVC Primer before gluing. You'll have leaks if you don't.
To get under the 30" sidewalk you can tunnel or if you don't like to dig you can jet the PVC under it. If you're not familiar with the procedure just ask and I'll walk you through the process. What problem do you have with your gas line? Ask it here and we'll try to answer you. As for your house piping 3/4" mains are normal, branching off into 1/2" supplies to the various fixtures. This will give you good service unless you tie more then three fixtures on a 1/2" branch and attempt to use them all at once. Cheers, Tom