    I have a Classic 90 Series Rheem RGRA series upflow/downflow furnace 3 years old. Intermittently, the furnace will not flame up or give out heat. Sometimes it only blows cold air. Sometimes, it locks out (middle green light flashing once then pausing). The furnace repair company came out and said it was the gas line pressure blowing out the flame. That has been ruled out by the gas company, who checked the inflow and outflow pressure. Are there any suggestions? The furnace is still under warranty.
  • Mar 4, 2007, 12:43 PM
    NorthernHeat
    Well, the service company should be replaced by someone who has a clue. Rheen/Ruud has had more than a few problems with faulty pressure switch's (5 year warranty) I don't know off the top of my head what 1 flash means, it is on the blower door though, also, if the furnace is not properly draining the water, it will act like a pressure switch issue. Good luck.
  • Mar 15, 2007, 09:47 AM
    dellav
    Quote:

    Originally Posted by tw5150
    I have a Classic 90 Series Rheem RGRA series upflow/downflow furnance 3 years old. Intermittently, the furnance will not flame up or give out heat. Sometimes it only blows cold air. Sometimes, it locks out (middle green light flashing once then pausing). The furnace repair company came out and said it was the gas line pressure blowing out the flame. That has been ruled out by the gas company, who checked the inflow and outflow pressure. Are there any suggestions? The furnace is still under warranty.

    We have same furnace and have had the same problem. Also ignition problem and now the furnace clanks/bangs just before fan comes on.
  • Mar 15, 2007, 07:14 PM
    T-Top
    Quote:

    Originally Posted by NorthernHeat
    Well, the service company should be replaced by someone who has a clue. Rheen/Ruud has had more than a few problems with faulty pressure switch's (5 year warranty) I don't know off the top of my head what 1 flash means, it is on the blower door tho, also, if the furnace is not properly draining the water, it will act like a pressure switch issue. Good luck.

    I agree with NorthernHeat check the drain lines on the furnace. Behind Top door two rubber lines going to drain trap left side of furnace. Trap will exit furnace behind lower door of furnace(blower door). Check for a kink in the line behind top door.(rubber line 1/2 inch)
  • Mar 20, 2007, 09:01 PM
    jaisen
    Quote:

    Originally Posted by tw5150
    I have a Classic 90 Series Rheem RGRA series upflow/downflow furnance 3 years old. Intermittently, the furnance will not flame up or give out heat. Sometimes it only blows cold air. Sometimes, it locks out (middle green light flashing once then pausing). The furnace repair company came out and said it was the gas line pressure blowing out the flame. That has been ruled out by the gas company, who checked the inflow and outflow pressure. Are there any suggestions? The furnace is still under warranty.

    New ignitor
  • Mar 21, 2007, 04:45 AM
    NorthernHeat
    Quote:

    Originally Posted by jaisen
    new ignitor

    If furnace is only 3 years old it has a spark ignitor, not hot surface and shouldn't need replaced. Installers often leave to many pvc filings in the pipes plugging the drain in the venting transition tee or in the trap, it seems to take 2 or 3 years to cause any problems.
  • Jan 30, 2011, 10:31 PM
    fixxedit
    The vacuum line had cracked on my rheem 90.(the one right inside the top panel) Snipped off half an inch, reconnected it, bingo!