Is 200 amp transfer switch is enough for two 200 amp panels to operate a 25ke generator.if the two panels are being inter connected.there is only one supply power from the single meter
![]() |
Is 200 amp transfer switch is enough for two 200 amp panels to operate a 25ke generator.if the two panels are being inter connected.there is only one supply power from the single meter
It would be Easier? To Interlock one Panel, hopefully your necessary circuits are in 1 Panel.
Do Both 200 Amp Panels have separate disconnects/Main Breakers?
Are you tieing both to the Main Lugs of 1?
Sounds like two 200 amp panels served by a 400 or 320 amp meter.
If this is the case, the ATS needs to be fully rated at 320 or 400 amp.