-   -   Is 200 amp transfer switch enough for two 200 amp panel (https://www.askmehelpdesk.com/showthread.php?t=682247)

  • Jul 13, 2012, 06:21 AM
    JOE956895
    Is 200 amp transfer switch enough for two 200 amp panel
    Is 200 amp transfer switch is enough for two 200 amp panels to operate a 25ke generator.if the two panels are being inter connected.there is only one supply power from the single meter
  • Jul 13, 2012, 06:36 AM
    Stratmando
    It would be Easier? To Interlock one Panel, hopefully your necessary circuits are in 1 Panel.
  • Jul 13, 2012, 06:54 AM
    JOE956895
    Quote:

    Originally Posted by Stratmando View Post
    It would be Easier? to Interlock one Panel, hopefully your necessary circuits are in 1 Panel.

    Actually what I am doing is connecting one of the 200 amp panel to the other one and then connecting the transfer switch to that panel.is it against the code or is thereany danger?
  • Jul 13, 2012, 07:13 AM
    Stratmando
    Do Both 200 Amp Panels have separate disconnects/Main Breakers?
    Are you tieing both to the Main Lugs of 1?
  • Jul 13, 2012, 07:23 AM
    tkrussell
    Sounds like two 200 amp panels served by a 400 or 320 amp meter.

    If this is the case, the ATS needs to be fully rated at 320 or 400 amp.
  • Jul 13, 2012, 01:09 PM
    stanfortyman
    Quote:

    Originally Posted by tkrussell View Post
    Sounds like two 200 amp panels served by a 400 or 320 amp meter.

    If this is the case, the ATS needs to be fully rated at 320 or 400 amp.

    Exactly.

    You CANNOT "interconnect" the two panels.

    You can use the 200A transfer sw to feed ONE panel.
    Or you can use a 400A transfer sw to feed both panels