Home ac blower not working
Home AC Blower and Outside Unit do not work. I can make the outside unit come on by pushing in the button on the Relay Switch on the outside unit. Both the Fan and the Compressor come on when the Relay Switch is tripped. There is no control voltage (25 Volts) from the Thermostat to the outside unit. Does the Blower have to run for the outside unit to run? Will the Low Pressure Switch prevent the Blower and the outside unit from running? I replaced the thermostat and checked that the Blower spins freely. I am thinking that the outside unit is fine and the problem is with the Blower. The control voltage from the Thermostat is prevented from going to the outside unit because the Blower is not running. Does this sound reasonable? Could the Low Pressure Switch be tripped, but why would this cause the Blower not to work? I am planning to replace the Capacitor on the Blower?