  • Jun 21, 2012, 10:52 AM
    0qwerty
    Goodman Heating Pump Parts
    I have a Goodman Split Unit Heat Pump that has a chattering Contactor. It is only getting 18 volts to the Contactor, but when you disconnect it, the voltage rises to 28 volts. I have put several Contactors of different brands on it with the same results.
    Any suggestions?
  • Jun 21, 2012, 11:38 AM
    hvac1000
    Quote:

    Originally Posted by 0qwerty View Post
    I have a Goodman Split Unit Heat Pump that has a chattering Contactor. It is only getting 18 volts to the Contactor, but when you disconnect it, the voltage rises to 28 volts. I have put several Contactors of different brands on it with the same results.
    Any suggestions?

    Could be a weak transformer, It might show voltage but not enough milliamps/VA. Use a minimum of 40 VA for the transformer. Now loose low voltage wiring can cause this and I have seen thermostats cause this problem also. Good luck.