Originally Posted by
massplumber2008
Hi Dukes
4" pipe requires, at a minimum, 1/8" slope per foot of pipe, so you would need 2" pitch for a 16' run of 4" sewer pipe.
You could also run the pipe at 1/4" pitch per foot of pipe (equals 4" pitch here), or at a maximum of 1/2" pitch per foot of pipe you could run the pipe with 8" pitch.
I recommend the 1/4" if possible, but if things are tight, 1/8" per foot of pipe works just fine!
Do NOT exceed the 1/2" pitch per foot of pipe as this sets the pipe up to clog as water rushes down the drain too fast leaving solids behind.
Mark