Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Trip setting of Vacuum circuit breaker? (https://www.askmehelpdesk.com/showthread.php?t=663394)

  • May 25, 2012, 03:22 AM
    amit00025
    Trip setting of Vacuum circuit breaker?
    I have a ABB Vacuum circuit breaker RMU IEC 60298, so its trip when load exceeds to set limit. Then I don't know how to set the trip setting of VCB or how to increase of load current setting of VCB?
    ]
    Amit
  • May 25, 2012, 05:13 AM
    tkrussell
    You will need to have a Short Circuit Corrdination Study performed by a qualified engineer for the system and/or circuit.

    Once this is done, the report will list the settings for this and any other distribution breakers.

    Any other method would be a guess, and if not guessed correctly, can be a serious hazard to the equipment, load, and personnel involved.