    I have a rheem unit I replaced the condenser motor and it is over heating then shuts done the old motor had 3wires coming from the motor brown black and orange the new motor had 4 wires 2 browns go to capasitor purple became come tied that to brown and black to black and I just tied of the orange it get kick on just fine blows cold air then motor get hot and shuts down don't want to blow motor
  • May 20, 2012, 11:24 AM
    Frank Mangrum
    Quote:

    Originally Posted by daviddodaro View Post
    I have a rheem unit I replaced the condenser motor and it is over heating then shuts done the old motor had 3wires coming from the motor brown black and orange the new motor had 4 wires 2 browns go to capasitor purple became come tied that to brown and black to black and I just tied of the orange it get kick on just fine blows cold air then motor get hot and shuts down don't want to blow motor

    You have wired your new motor incorrectly. The motor lead you will not use is the brown with white trace marks--cap this wire either with wire nut or electrical tape. Connect solid brown wire to capacitor (FAN) terminal--- then connect purple wire where old motors orange wire was connected--- then connect black to black.
  • May 21, 2012, 08:23 AM
    thermalmedics
    He is right on about the rewire

    In the future and for all who read this going forward:

    stop the 3 wire madness when re-doing condenser fan motors.

    Just go to 4 wires - it is so easy and motors like it so much more

    Br - br/wht to new cap

    Purp and blk to load side of contactor or one to contactor and one to relay on defrost board if a heat pump

    Just leave the dual run capacitor in place and it now just powers the compressor.

    more better and thats how its done in the field
  • May 21, 2012, 05:04 PM
    Frank Mangrum
    Quote:

    Originally Posted by thermalmedics View Post
    he is right on about the rewire

    in the future and for all who read this going forward:

    stop the 3 wire madness when re-doing condenser fan motors.

    just go to 4 wires - it is so easy and motors like it so much more

    br - br/wht to new cap

    purp and blk to load side of contactor or one to contactor and one to relay on defrost board if a heat pump

    just leave the dual run capacitor in place and it now just powers the compressor.

    more better and thats how its done in the field

    When working in the field we should be "more better". One should strive to keep customers equipment original as possible for a couple reasons: Wires match OEM wiring diagrams--and where do you put this now extra capicitor in a tight control box --Remember voltages (Back EMF) at this extra capacitor terminals can be 370 to 440 volts while motor is running. "4 wire---Motors like it so much more"-- I don't understand?