I have a 100a 600v 3phase service, I need 135000w of equipment feed from it some are 120 some are 208 3phase. Can that service handle the load
![]() |
I have a 100a 600v 3phase service, I need 135000w of equipment feed from it some are 120 some are 208 3phase. Can that service handle the load
Based on the raw numbers given, no it cannot...
First where are you that you have a 600V electrical service?
Or is it really 208V, 240V or 480V?
Knowing this greatly effects the numbers.