I would like to upgrade service panel at commercial location to accommodate 5 100-Amp Service Panels (4 Apts. & 1 House Panel) & 1 200-Amp Service Panel.
I asked about upgrading the service equipment a couple months ago and TK asked me to check with the utility company to get some answers before proceeding. TO answer his questions:
1. ringed or ringless meter sockets?
It's up to me (I do not know what the difference is - if someone could let me know I would appreciate it).
2. Location of meters?
The utility company has no problem with the service panels & meters being located inside.
3. Lever bypass?
A lever bypass is not required for small commercial.
I did some research and found a Cutler Hammer 6 meter pack with 200 socket amp rating, ring style, 6 meter sockets, 600 bus ampacity. Catalog Number is CH1MP6206R. After doing the load calculations, I feel comfortable with 600 amp.
http://images.i2content.net/MRO_imag..._4_5_6_5_8.pdf
1. Is this meter pack a good choice?
2. Will this ringed meter pack work with the meters shown?
3. Do the feeders going to the bottom 2 service panels need to be secured to the plywood or are they okay as is?
4. What gauge wire is coming into the current main disconnect? Will this work with a 600 Amp Meter Pack?