Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Outdoor compressor runs, but fan doesn't? (https://www.askmehelpdesk.com/showthread.php?t=655920)

  • Apr 30, 2012, 11:14 AM
    lloyd212
    Outdoor compressor runs, but fan doesn't?
    Compressor runs, but fan doesn't. Two different capacitors, (45, 7.5) both read 0.1 MFD. I check with Ohmeter, 7.5 capacitor is reading 37... 45 capacitor reads 2.4... Fan blade turns freely. What could the problem be?
  • Apr 30, 2012, 11:39 AM
    Stratmando
    You can't check capacitance with resistance. If it is an analog meter, you can get an Idea if it may be good by placing probes on capacitor in resistance scale, each time you reverse the leads, you should see the needle swing over then drob back, and repeating every time you swap leads. That is the Capacitor charging, discharging.

    It may be the capacitor. Resistance will tell if a cap is shorted.
    If you can't test it, replacing should be relatively cheap.