  • Apr 21, 2012, 02:02 PM
    joeirna
    Electrical conduit wire capacity
    Can I put 3#10 and 3#14 wires with a ground in a 3/4" conduit? The conduit is underground between two buildings, is this okay?
  • Apr 21, 2012, 03:06 PM
    stanfortyman
    What kind of conduit?
  • Apr 22, 2012, 03:36 AM
    tkrussell
    And what type of insulation on the wires?
  • Apr 22, 2012, 05:04 AM
    stanfortyman
    And why so many conductors?
    Are you aware that you can only have one circuit maximum at a detached structure? After that you need a feeder and sub-panel.
  • Apr 22, 2012, 06:09 AM
    joeirna
    Electrical conduit wire capacity
    I asked about the 3#10 and 3#14 wires in a 3/4" conduit. The details are as follows: the conduit is grey plastic pipe, the insulation is thwn on the wires, the #10 wires will feed a sub panel from a 30 amp breaker in the main panel, the sub panel will have its own grounding rod and separated ground from the neutral. The #14 wires are for an outside lighting fixture that will be controlled by 3way switches, one in the house and one in the garage. The pipe is about 35 feet long and is buried 4 feet deep in the ground. There will also be a bare copper ground wire along with the insulated conductors in the pipe. The question is, is this okay to do? Thanks for your time and expertise.
  • Apr 22, 2012, 06:17 AM
    stanfortyman
    3/4" is fine for this, although I would have gone to 1" myself.
  • Apr 22, 2012, 06:22 AM
    Stratmando
    I would use an insulated #10 for ground, stranded on all?