  • Mar 20, 2012, 03:31 AM
    J4Baggers
    Smoke coming from ground rod?
    My 250kva generator is earth however there is now smoke coming from the pit that the generator is earthed
  • Mar 20, 2012, 04:14 AM
    tkrussell
    Using an clamp on amp meter , measure the ground wire connecting to the rod, to determine if any current is flowing.

    That will need to be corrected.

    Could be a poor soil condition causing the ground resitance to be too high, still should not have high amps flowing to ground thou.

    There is a clamp on ground rod resistance instrument available to measure the resistance of the rod.
  • Mar 20, 2012, 06:32 AM
    hfcarson
    J4, along with the recommendations of TK, you should be carefully reviewing the
    Grounding and if the neutral to ground connections are correct. If this is not a separately
    Derived system, the neutral should not be bonded to the ground. This may have something to do
    With the "hot" ground rod if installed incorrectly.