  • Mar 11, 2012, 11:58 AM
    nairb16003
    Honeywell programmable thermostat
    Thermostat will not shut down furnace when switched to "off" position, but will shut down when set temperature is met.
  • Mar 11, 2012, 06:50 PM
    ballengerb1
    What model do you have?
  • Mar 11, 2012, 07:23 PM
    nairb16003
    Honeywell RTH2300/RTH221
  • Mar 11, 2012, 07:30 PM
    ballengerb1
    Just to get started this may help RTH2300B I did not recall that you can shut this stat to an OFF position, can you?
  • Mar 12, 2012, 01:41 PM
    nairb16003
    Yes. On the bottom left side of the thermostat there is a "Heat", "Off" and "Cool" position where you can slide the switch. On the bottom right side there is a switch you can slide the fan to "Auto" or "On".
  • Mar 12, 2012, 01:44 PM
    nairb16003
    Also the link you posted is the correct thermostat. The picture on that page is the same thermostat that I have. If you look at the bottom right and left of the picture of the thermostat you will see the print of what I was trying to explain on the above post.
  • Mar 13, 2012, 01:03 PM
    nairb16003
    Well, I guess we can forget all I wrote above. I woke up this morning and only my blower motor was running on the furnace as well as my condenser outside. I shut off everything. Shut off breaker to condensing unit and unhooked my 2 wires from the furnace board that controls the contactor on the condenser. Tried to restart the furnace, but the vent motor comes on for about 3 seconds and shuts down. After a couple more seconds the blower motor comes on. Any help?
  • Mar 13, 2012, 02:50 PM
    ballengerb1
    I am stumped, maybe time to make a call, sorry
  • Mar 13, 2012, 05:03 PM
    mygirlsdad77
    Is this a new stat? If so, are you sure it is wired correctly. Let me know if its new, or has been in use and worked correctly before. Also, I need to know if you have a heat pump system, or just conventional forced hot air gas furnace with central air conditioning. Just a heads up, if it's a heat pump, Im afraid I will be of no real use to you. If it's a conventional system, depending on the brand and year, I may be able to at least point you in the right direction. Or, as ballengerb suggested, make a call to a local tech and they should be able to get you fixed right up. Please do let us know either way.
  • Mar 13, 2012, 06:54 PM
    nairb16003
    I found out the problem! I did some voltage testing on the vent motor as well as the transformer. Then I went to the control board of my furnace and checked the voltage from Red to White as well as Common to Red. I had 24v from R to W, but not C to R. So I took the face off the base of the thermostat and found that a battery had exploded inside. Not sure if something caused this or if the battery was just garbage. Needless to say I went and bought a new thermostat and now have heat! Thank you very much for taking the time out of your day to help!
  • Mar 14, 2012, 04:06 PM
    mygirlsdad77
    Hey, just glad you got it fixed. Good job, and thanks for the update.