-   -   Replacing Weathertron thermostat with Honeywell (https://www.askmehelpdesk.com/showthread.php?t=64065)

  • Feb 18, 2007, 09:30 PM
    freemom06
    Replacing Weathertron thermostat with Honeywell
    I am attempting to replace our Weathertron thermostat with a Honeywell RTH3100C. We have a Trane heatpump system. I am having trouble with the wiring. My wires don't match the 'less common wire designations' in the manual.
    I have the following wires on the Weathertron:
    R-red
    T-brown
    O-orange
    G-green
    Y-yellow
    X2-black
    B-blue
    W-white
    F-Pink
    and a grey wire I don't think was connected to anything-it is not taped off, and we don't remember disconnecting it, it just suddenly appeared after we took off the wire plate.

    Here is what I have based on the Honeywell installation guide:
    E=Weathertron X2
    Aux=Weathertron W
    Y=Weathertron Y
    G=Weathertron G or F (not sure which one to do)
    O=Weathertron O
    L=Weathertron F
    R=Weathertron R
    B=Weathertron B (not sure which one to do)
    C=Weathertron B

    I'm not sure where the T wire should go or what to do with the grey wire.

    Thanks for the help.
  • Oct 11, 2007, 07:17 PM
    jcovey
    I am replacing a Weathertron with a Honeywell RTH230B and need to know the appropriate wiring configuration?
  • Jul 16, 2008, 01:04 PM
    Donald Tanner
    Do you have schematic for the Honeywell RTH3100C?
  • Jul 16, 2008, 05:24 PM
    hvac1000
    2 Attachment(s)
    Quote:

    Originally Posted by freemom06
    I am attempting to replace our Weathertron thermostat with a Honeywell RTH3100C. We have a Trane heatpump system. I am having trouble with the wiring. My wires don't match the 'less common wire designations' in the manual.
    I have the following wires on the Weathertron:
    R-red
    T-brown
    O-orange
    G-green
    Y-yellow
    X2-black
    B-blue
    W-white
    F-Pink
    and a grey wire I don't think was connected to anything-it is not taped off, and we don't remember disconnecting it, it just suddenly appeared after we took off the wire plate.

    Here is what I have based on the Honeywell installation guide:
    E=Weathertron X2
    Aux=Weathertron W
    Y=Weathertron Y
    G=Weathertron G or F (not sure which one to do)
    O=Weathertron O
    L=Weathertron F
    R=Weathertron R
    B=Weathertron B (not sure which one to do)
    C=Weathertron B

    I'm not sure where the T wire should go or what to do with the grey wire.

    Thanks for the help.

    Here you go on Weathertron/same as Trane
  • Jul 16, 2008, 05:26 PM
    hvac1000
    Honeywell


    http://customer.honeywell.com/techli.../69-1889EF.pdf
  • Feb 2, 2009, 05:30 PM
    callmerr4305
    I have an old Weathertron thermostat. I just purchased a Honeywell RTH 230B programmable thermostat to replace it. Honeywell have 5 wires RH, RC, W, Y, G. But my old unit utilized 8 wires. G-green, Y-yellow, X2-black, B-blue, U_W-white, O-orange, R-red, T-brown.
  • Feb 2, 2009, 05:43 PM
    hvac1000
    See this

    http://customer.honeywell.com/techli...0s/69-1800.pdf

    The thermostat you have will not work with your system. You need a heat pump thermostat. READ number 1 Introduction to see what I mean.
  • Aug 8, 2012, 10:59 AM
    meme41
    I have a old trane mercury thermostat BAYSTAT239A trying to replace it with a honeywell thermostat RTH11B need help with wiring ?