  • Feb 24, 2012, 06:22 AM
    mrjr1
    Sub panel rewire
    I want move a ground from bus bar in sub panel with other ground wires
  • Feb 24, 2012, 06:33 AM
    tkrussell
    OK, you need to move a ground from a bus bar.

    Please explain further, as we do not know what your queston is.
  • Feb 24, 2012, 08:43 AM
    donf
    Good morning, please do not open a new thread to add more information.Just continue the existing thread by way of the "Quick Answer" box. Thanks, Don

    We need more information from you because your question leaves a awful lot to guess at.

    For example, is this secondary panelboard within the same building as the main service panelboard?

    Is the Neutral in the secondary panelboard isolated from "ground"?

    Most importantaly is why do you believe you need remove a ground from the ground bus?
  • Feb 24, 2012, 03:44 PM
    mrjr1
    Thank you for your time, the secondary panel board IS NOT within the same building. YES, the neutral is isolated from ground. Last answer is that at home inspection it is noted that two double-throws replaced two single-throws, the ground from these two switches are ran to the bus bar and home inspector suggests that it be moved with other grounding wires.