  • Feb 20, 2012, 06:56 AM
    davenmoni
    Two 120 amp tankless hot water units in single 200 amp home
    My home has two water lines and therefore two hot water tanks. I just replaced one with the ECO27 unit and can barely make the space for the three 40 amp double pole breakers needed. I am trying to think ahead as I will likely want to replace our main tank as well. Our house is 100% electric with separate radiant systems in each room. My 200 amp main panel has a couple circuits which could be moved into my basement panel. I currently have a 100 amp sub panel in the basement and another one on the second floor. The second unit would be near the basement sub panel. How should I run the next 3 40 amp double pole breakers to the second unit and do I run the risk of my entire house shutting down?
  • Feb 20, 2012, 07:35 AM
    tkrussell
    A 200 amp service cannot handle the added load of a tankless water heater.
  • Feb 20, 2012, 08:55 AM
    davenmoni
    I believe you as you have great knowledge, but why do the instructions say 200 amp service is required and what options do I have?
  • Feb 21, 2012, 05:51 AM
    tkrussell
    I believe the water heater needs a 200 amp service alone, not including the existing load.

    Have an electrician do a service rating calculation to confirm.

    You may need to go to a 400 amp service.
  • Feb 27, 2012, 10:23 PM
    sinnadurai
    Do a load calculation in a MS exel work sheet with load(amp)in Y-axis and time(clock) in X-axis. Calculate the maximum load by adding loads in vertical column,which gives the main breaker size. If it exceed 200Amps contact the utility.
  • Feb 28, 2012, 07:09 AM
    tkrussell
    Assuming the question is regarding a home in the USA or Canada, service rating calculations is not done in the fashion:

    Quote:

    Originally Posted by sinnadurai View Post
    Do a load calculation in a MS exel work sheet with load(amp)in Y-axis and time(clock) in X-axis. Calculate the maximum load by adding loads in vertical column,which gives the main breaker size. If it exceed 200Amps contact the utility.

    There are derating factors used by the National Electric Code and the Canadian Electric Code that will arrive at a service rating less than the total sum of actual loads.

    Davenmoni, the original poster, needs to have a local electrician do a service rating calculation to confirm the size service needed.
  • Feb 28, 2012, 10:35 PM
    sinnadurai
    tkrussell,When I mentioned load it include factors like diversity/simultaneous/derating etc. Anyone in electrical engineering field should know it.
  • Feb 29, 2012, 03:34 AM
    tkrussell
    That may be, but the poster is a homeowner, not an engineer.