    Janitrol furnace inducer motor starts, burners start then shuts down
    It is a GMP-125-4
    Inducer motor starts, I can see the igniter glowing and all the burners start for a few seconds.
    Then it shuts down the status light on the control board goes out.
    If I restart the furnace again right away the burners only light for a split second
  • Feb 11, 2012, 05:13 PM
    mygirlsdad77
    Clean or replace the flame senser
  • Feb 11, 2012, 06:04 PM
    bajaexpl
    Thank you but I already cleaned the flame senser. I replaced the controller board and that solved the problem
  • Feb 11, 2012, 06:17 PM
    mygirlsdad77
    Just glad you got it fixed. Good job.