Burner won't shut off when temp is reached
![]() |
Burner won't shut off when temp is reached
Usually that is a thermostat problem. But it can also be a relay contained in the furnace safety device. IE cad cell primary or stack switch. To test remove one of the thermostat wires off the burner control. If it shuts off you have found a bad thermostat on a pinched thermostat wire. If it keeps running then you have a bad primary or stack control depending on what kind of safety device came on the unit.
All times are GMT -7. The time now is 01:34 AM. |