Have checked element, 11 ohms Do not think element is the problem
Where do I find the thermal limiter or is there an overheat fuse , the unit runs but very little heat
Thanks , homehunter
![]() |
Have checked element, 11 ohms Do not think element is the problem
Where do I find the thermal limiter or is there an overheat fuse , the unit runs but very little heat
Thanks , homehunter
With that resistance you should draw 22 amps of current. It's most likely stopped up with dirt.