When the panel is 25 ft from the meter do you need a 200amp breaker close to the meter
|  | 
When the panel is 25 ft from the meter do you need a 200amp breaker close to the meter
Plan on running two no. 4,0 aluminum with no. 6 wag copper inside 2 inch PVC 20 ft. Inside to main breaker
If you mean 20' inside then that is way too much. You'll need a main disconnect/breaker either outside or just inside the structure.
Most areas require it within 5-6 feet of where the service enters. Only your local code office can tell you this for sure.