    Electrical Sub Panel can I run a reduced neutral wire for 100 amp?
    What size wire do I need to run a 100 amp sub-panel, I have #2 Aluminum 2-2-4 # 4 is the neutral
  • Jan 25, 2012, 03:15 PM
    stanfortyman
    That's fine, but you need a ground also.
    You can use #8cu or #6al for the ground.