What size wire do I need to run a 100 amp sub-panel, I have #2 Aluminum 2-2-4 # 4 is the neutral
![]() |
What size wire do I need to run a 100 amp sub-panel, I have #2 Aluminum 2-2-4 # 4 is the neutral
That's fine, but you need a ground also.
You can use #8cu or #6al for the ground.