Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical Engineering (https://www.askmehelpdesk.com/forumdisplay.php?f=497)
-   -   Voltage drop (https://www.askmehelpdesk.com/showthread.php?t=626701)

  • Jan 10, 2012, 07:47 PM
    jaime05121970
    Voltage drop
    I have to feed a pump it has a load of 30 amps, is 115 volts and is located 1300 feet.
  • Jan 10, 2012, 08:30 PM
    ballengerb1
    You have not given us all the info we would need to be accurate by try this calculator for yourself. Voltage Drop Calculator 2 awg aluminium would give you about a 9% drop in voltage.
  • Jan 11, 2012, 05:29 AM
    tkrussell
    I am not sure how Ballenger came up with 9% Vd with #2 Al.

    Using the same calculator I arrive at 17.7 % Vd using #2 Al at 120 volts, 30 amp load, 1300 feet.

    Recommended voltage drop is 3%, and I arrive at needing 1000 MCM Al wire ,using this calculator:

    Voltage Drop Calculator

    In any case, you need to look into using transformers at both ends to step up to a higher voltage at the feed end and as tep down transformer at the load end.

    Trying to deliver 120 volts 1300 feet is not practical.