  • Jan 10, 2012, 09:13 AM
    danny0427
    In a nursing home, what is the distance from water (a fixed commercial dishwasher)
    In a nursing home, what is the distance from water ( a fixed commercial dishwasher ) from a panelboard (3ph 208V)?
  • Jan 10, 2012, 09:50 AM
    tkrussell
    Does not matter what location or facility, a panelboard shall have minimum of 30 inch wide clearance in front of panel, and does not need to be center of panel.

    If the panelboard is wider than 30 inch, then that dimension is the clearance.