Building not connected in anyway. Is it o.k. To have seperat grounding (ufer).
![]() |
Building not connected in anyway. Is it o.k. To have seperat grounding (ufer).
A grounding electrode is required if the building is served by a feeder, as opposed to only one circuit. A ufer is a preferred electrode, and if you have one that's all you need.
This however has nothing to do with the equipment ground that must also be run with the feeder.