  • Feb 12, 2007, 06:17 PM
    racecar
    How to wire two thermostats to run one circulating pump
    How do you wire two 24v thermostats in two different zones that will run one 110v circulating pump?
    Thanks
  • Feb 12, 2007, 07:26 PM
    ballengerb1
    If you system was properly installed each zone has a solenoid on the hot water manifold. One stat goes to one solenoid and the other stat to the remaining solenoid.
  • Feb 12, 2007, 08:27 PM
    labman
    In a zone system, the thermostat has 2 jobs, fire up the boiler and open the zone valve. The circulating pump should be wired to the circuit that fires up the boiler. In some systems, then the valve opens, it makes a circuit to fire the boiler. Check the sticky at the top of the heating forum for more details.
  • Feb 12, 2007, 08:56 PM
    NorthernHeat
    Each thermostat should control a zone valve, when the valve opens an end switch closes turning on the boiler and/or circ' pump.