Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Electrical wiring for garage (https://www.askmehelpdesk.com/showthread.php?t=623782)

  • Dec 31, 2011, 06:51 PM
    Sterli12
    Electrical wiring for garage
    I have a 200 amp max per bar breaker in my home and I would like to run power for outlets in my garage. I am thinking 60 amp box with 20 amp gfci outlets. I am not sure if I should use 8 or 6 gage wire fom my breaker to the new one, also, hat type of box should I use in the garage? Also, I am wondering how to wire up the gfci outlets? Thanks!
  • Jan 1, 2012, 05:23 AM
    tkrussell
    Assuming NM-B cable (Romex) you cans use #6-3 plug ground and use a 50 amp breaker to feed the new panel.

    What type of construction will dictate what type of box is used for the new outlets.

    How to wire GFI outlets? Same as a standard outlet.

    The new panel will need a separate equipment ground bar accessory to keep grounds and neutrals separated in the new panel, and do not install neutral bonding jumper.

    If the garage is a separate building , at least one ground rod will need to be installed and connect to the equipment ground bar using # 6 copper wire.