    500feet to my barn .100amp service at my home what size alum, wire do I need for 100amp service in my barn Thanks .
  • Dec 24, 2011, 04:24 AM
    tkrussell
    500 feet is too far to deliver 120/240 volts.

    Assuming a 50 amp load at 240 volts, you would need #3/0 aluminum.

    I suggest you bring in an electrician to evaluate the actual load, and design a transformer system.