Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Appliances (https://www.askmehelpdesk.com/forumdisplay.php?f=157)
-   -   Rheem Gas Furnace RGPH - Blower Motor does not run - (https://www.askmehelpdesk.com/showthread.php?t=620206)

  • Dec 16, 2011, 06:26 PM
    AaronL
    Rheem Gas Furnace RGPH - Blower Motor does not run -
    Hi,

    I received some great help here before with my plumbing so I'm back to solve a furnace problem. Thanks for looking.

    Unit Information:
    Rheem RGPH-05NAUER
    Serial # FD5D302F310005868
    Natural Gas, Induced draft, upflow/horizontal
    Installed in the year 2000

    2 days ago the blower motor stopped working. I referenced the owners manual and used the troubleshooting flowchart to diagnose the problem. I climbed up into the attic access hole and found the furnace so I was able to verify all the operations with my own eyes. After following all the steps the flowchart indicates "replace blower motor."

    I completed the following steps up in the attic
    1. Set thermostat for heat
    2. Induced draft motor starts (
    3. Spark energizes (I can hear the clicking sound)
    4. Main burners light (I can see the clean blue flames from both burners)
    5. Indoor blower DOES NOT start (20 sec. After main burner ignites)
    6. Test IFC (Integrated Furnace Control) for 120 volts between HEAT and COMMON terminals. Confirmed 120VAC between HEAT and COMMON terminals. Flowchart indicates "replace blower motor."

    I called a few HVAC repair techs. This being Friday afternoon, I only reached 1 on the phone. He suggested that I try to identify if the "start capacitor" was faulty by trying to spin the motor by hand to get it to start. I will try this tonight.

    Without seeing the unit himself, he quoted $475 to replace the blower motor. When asked, he said the parts cost would be $150-175.

    Does his advice seem accurate?

    Is there anything else I can check?

    Thanks,
    Aaron

  • All times are GMT -7. The time now is 05:11 AM.