  • Dec 5, 2011, 09:33 AM
    halbaker
    Goodman blower time delay relay?
    There is a 6 minute delay from when my heat pump compressor comes on until the inside blower comes on. It used to only delay a few seconds. This is a Goodman A60-20 air handler. Do I need to replace the blower time delay relay?
  • Dec 6, 2011, 05:38 AM
    drtom4444
    I would just eliminate it. Just hook common and "G" directly to the fan relay and that will fix it. It should only be a few seconds, but basically it's a useless feature. Normally, the time delay is wired to run the fan a few minutes after the compressor turns off to get the chilled air out of the unit.