Goodman GKS9 Furnace Induction motor issue?
Goodman GKS9 furnace is giving issues. The LED flashes 3 times which the manual says is caused by blocked flue, blocked air inlet, pressure switch hose, or bad pressure switch. Induction motor works fine. I snaked both outside air lines, blew out the pressure switch hose, and finally replaced the pressure switch. Still same problem.
After further troubleshooting, I discovered that if I turned the furnace power off, waited for the induction motor to wind down, and restarted the furnace with the cover off everything started normally. I could hear the pressure switch operating as the motor spun up. I then put the cover back on and it worked fine.
The only thing I can imagine is that induction motor is weak and needs less intake resistance afforded by the cover being off allowed the pressure switch to close normally.
Any ideas? Thanks!