Carrier 8000 short cycles
My Carrier 8000 gas furnace was used to replace the oil furnace which had 4"ducting. The ducting was replaced with 6" but the 4" registers were not changed. I replaced half of the 4" registers with 6" and the short cycles stopped. Now after 5 years they have returned. I found I have to be careful and not install a filter that is too restrictive or that contributes to the short cycles. Is thare anything else that could be done to stop the short cycles? My return vent is 14" x 25"
Thanks,
Dave