Heil n8mpn furnace troubleshooting?
Heil N8MPN. Fires up properly. Shuts down circulating fan and burners after 15 seconds to several minutes. Draft inducer continues to run for short period, kicks out then immediately kicks back on and then unit goes back through same sequence. Honeywell valve shows proper function with heartbeat geen light. Checked chimney for proper draft and even pulled flue from chimney and trtied with flue freely venting in basement. Same results. Filter is clean and vaccumed out around burners. Sensor tube looks good with no visible cracks. Unit worked fine to end of last heating season.