  • Oct 30, 2011, 04:06 AM
    meerahvac
    Static pressure
    How to find static pressure in duct system during commissioning?
  • Oct 31, 2011, 08:50 AM
    SpringtimeHomes
    Sounds like its too late but should have done Energy Star certification with a Manual J. A mechanical engineer who does residential or commercial forced air systems should be able to help you out.
  • Oct 31, 2011, 03:09 PM
    ma0641
    You need to have a pressure/vacuum gauge and a pitot set to do this. Typically you will drill a small 1/8" hole in the supply side and return side ductwork, insert the pitot and measure the pressures. One will be positive and one negative. Then you add the two of them and compare it to the figures on the data plate of the air handler.