Ok... I am wanting to run a 60 amp subpanel in my attached garage. My main breaker panel, located in my basement is 200amp. I am planning on having a Siemens 60amp 2-Pole Breaker in my main panel (Basement)- then run #6 THHN Cooper Wire to my subpanel in 1-1/4" Conduit. Will be running 2 Hots (Black/Red), 1 Neutral (White)and Ground Wire. I will be using A 125 main lug panel, and put a "Main 60amp 2-Pole Breaker" into two slots (Panel has 12 slots total). I will wire the hots to the breaker, which will feed the hot bus bar- and act as a main breaker for the rest of the breakers I add later. Some of my questions. In my plastic conduit,can I and do I use a bare solid copper ground, what size....6 or 4? Or can I run ground wire that is covered/insulated #6? The subpanel will be approx 35feet away from main. The reason I am hooking up a "Main Breaker" in the subpanel,is to be able to shut off power to the subpanel without going downstairs. Any insite will help.