  • Oct 19, 2011, 04:14 PM
    charliek1011
    My gas furnace keeps running well after it passes the set temp.
    I set the desired temp on the termostat ( 70 F ) and the furnace keeps going until we get to 90F. It blows hot no matter what... It eventually kicks off but sometimes it takes hours...
  • Oct 19, 2011, 05:52 PM
    JonesHVAC
    Brand and model of furnace please. Thank you.
  • Oct 19, 2011, 08:09 PM
    charliek1011
    Brand : Goodman Model number CAPF4860C6BA
  • Oct 20, 2011, 05:05 AM
    JonesHVAC
    Your model number is inside the furnace... that happens to be the model number to the indoor coil that sits on top of the furnace for your A/C. Try this in the mean time... remove the stat --> jumper the red and white wires to call for heat --> let furnace cycle a bit and then un jumper the wires. Let me know if the furnace cuts off. I think your stat is bad.
  • Oct 20, 2011, 06:09 PM
    Bigstew
    My York furnace just keeps on running after the set temp
  • Oct 20, 2011, 06:27 PM
    JonesHVAC
    BigStew, try the same as I suggested to Charlie.