Turned the furnace on to get ready for winter everything worked fine but it did not ignite the glo ignigter lit up and it clicked to let the gas on and nothing happened and I have no code a flashing , the red led light. Can anyone help bryan
![]() |
Turned the furnace on to get ready for winter everything worked fine but it did not ignite the glo ignigter lit up and it clicked to let the gas on and nothing happened and I have no code a flashing , the red led light. Can anyone help bryan
Are you sure it clicked to let gas on, or did it click to shut the igniter back off? Did you actually hear gas flow? Does your unit have a condensate trap on the outside with two black tubes going into it from inside the furnace? If so, is there water in the trap? If not, full it with water and see if the furnace starts up. Im assuming your furnace is a 90+. Do you have a plastic or metal vent? Actually, if you could give the model number of the unit it would help.
It's a metal vent model number is GMT090-3A
Ok, this establishes an 90,000 BTU 80% efficient furnace. Do you have and can you use a multi-meter?
Yes
Set the meter to continuity and unplug the harness (or remove both wires) from board. Check to see if you have continuity and if you don't replace the ignitor. If you do then set the meter to voltage and check the board while stat is calling for heat... let it cycle as you will only get 120v when it calls for ignition.
Sorry, I forgot to put in there you are removing wires / harness for the ignitor... getting late here, lol.
Thanks for the help
Your welcome, was it the igniter or the board?
Igniter
Sorry I was confused. In your original post, you said "the glo igniter lit up". Or did I mis-interpret the sentence? Either way, glad your up and running.
Mygirlsdad77: I got you covered bud! ;)