-   -   Sub-panels with 50 amp outlet and breakers being fed by two pole 100 amp main service (https://www.askmehelpdesk.com/showthread.php?t=600782)

  • Oct 3, 2011, 09:24 PM
    joaquin13
    Sub-panels with 50 amp outlet and breakers being fed by two pole 100 amp main service
    I have a number of sub-panels with a 50 amp breaker for a 50 amp RV outlet being fed by a two pole 100 amp main service 120/240, I want to know how many 50 amp outlets I can safely install, will I need to upgrade the main service panel to accommodate more 50 amp RV outlets?
  • Oct 4, 2011, 01:48 AM
    donf
    Define "Number" of secondary panelboards, please.

    Also, define the number of RVs plugged in at one time and the average amperage used by each RV.
  • Oct 4, 2011, 05:34 AM
    tkrussell
    If this is a RV park, you need to contact an electrical contractor to come in and review the site and size the electrical distribution system.

    There is a entire section, Article 551 of the National Electric Code, dedicated for RV parks.
  • Oct 4, 2011, 11:21 AM
    stanfortyman
    You can literally install as many receptacles as you want.

    TK's answer is the only correct one. This is NOT a DIY project.