  • Oct 2, 2011, 02:04 PM
    pribanic1103
    1 Attachment(s)
    No neutral bus in FP electric panel, what can I do?
    I do know I need to upgrade the box but I need to install my electric dryer immediately for use. I have the breaker ready to install but have come across the problem of I see no neutral bus bar for the neutral wire. What can I do or can I install a bar on my own?
  • Oct 2, 2011, 02:09 PM
    stanfortyman
    That bar IS your neutral bar.

    What is that panel to the left?
    Where are those extra wires going from the right?
  • Oct 2, 2011, 02:18 PM
    pribanic1103
    We also have a glass fuse panel connected. Now can I attach both the ground & neutral wires to the bar? I though it was a ground bar because of the green lug screw.
  • Oct 2, 2011, 02:34 PM
    stanfortyman
    That bar is bonded to the panel box so it acts as both the ground and neutral bar.
  • Oct 3, 2011, 05:24 AM
    donf
    If this panelboard is a secondary panelboard, then you must have a four wire feed to it and you must not connect Neutral and Ground to the same bar. So the secondary panelboard else needs a ground bar.