-   -   Is it possible to place three 1phase transformers instead of 3phase transformer (https://www.askmehelpdesk.com/showthread.php?t=599498)

  • Sep 28, 2011, 06:51 PM
    sudharshan.g
    Is it possible to place three 1phase transformers instead of 3phase transformer
    Transformers
  • Sep 28, 2011, 06:54 PM
    stanfortyman
    No, it is not.
  • Sep 29, 2011, 04:39 AM
    tkrussell
    Stan, did you mis-read the question?

    Using three single phase transformers in place of a 3 phase unit has been done many times.

    A 3 phase transformer is nothing more than 3 - 1 phase transfomers in one cabinet, connected in a Delta or Wye configuration.
  • Sep 29, 2011, 01:31 PM
    stanfortyman
    Wow, I've never seen it done, and I figure it violates keeping all circuit conductors in the same raceway, etc, codes.

    I have done quite a bit of commercial/industrial work over the years, but have yet to see this.
    Good to know.
  • Sep 30, 2011, 02:36 AM
    tkrussell
    1 Attachment(s)
    Ever see a cluster of three pole mounted kettles? Those would be three single phase xfers for a 3 phase service.