    Bryant Evolution System Malfunction?
    My 18 month old Bryant Evolution A/C giving this message on thermostat. Malfunction Alert. Error code: indoor unit communication fault 255 events active. What does this mean? How to reset? A/C not working at this time.
  • Sep 24, 2011, 07:16 PM
    T-Top
    For some reason the user interface(thermostat) has lost communication with the fan coil. Loose wire connection at thermostat or control board will do it. Or a control board going bad. The system should be under warranty have your service company check it out.
  • Sep 25, 2011, 10:26 AM
    BobSch
    You are correct. It was the control board, which got moisture on it from a small pinhole opening. The installer said it was his error (duh) and has taken care of it.