    The wife turned on the toaster this morning and the thing quit and the receptacle was melted a bit,the breaker never tripped, fridges outlet does not work along with two in the living room. I replaced the melted receptacle. Still nothing on all four outlets the NEUTRAL reads 120 volts with ground HOT reads the same 120 with ground but HOT and NEUTRAL read 0 I used a analyzer and it reads HOT/GRD reverse on all four outlets. What's going on house is 10yrs old

    I called a pro but he can't make it till next weekend

    Thanks

    skyhogg
  • Feb 3, 2007, 04:37 PM
    tkrussell
    I think the neutral wire is broken someplace. Is this circuit a shared neutral for two circuits?

    If you open akl these kitchen outlets, you may find one with a red and black, this is the feed from the panel, and the neutral white splice can be broken or loose here

    Or can just be a broken neutral for a two wire circuit. Do the outlets connect with the wires pushed into small holes on the back of the devices. These connections are popular cause of loose or open connections.
  • Feb 3, 2007, 04:51 PM
    skyhogg
    All four outlets are on the same 20amp breaker tried changing the wire in the broken box to see if the problem moved to other outlets but it didn't. I don't know about the shared neutral or two circuits.

    Skyhogg
  • Feb 3, 2007, 05:03 PM
    skyhogg
    OOP"S breaker box not broken Box
  • Feb 3, 2007, 07:30 PM
    tkrussell
    There is a break in the neutral someplace.
  • Feb 3, 2007, 08:38 PM
    skyhogg
    Thanks I will have the pro look at it.

    skyhogg
  • Feb 4, 2007, 05:12 AM
    tkrussell
    Great, let us know what is found.