Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   What should I do if a main breaker is tripping, but we just replaced it a year ago? (https://www.askmehelpdesk.com/showthread.php?t=597511)

  • Sep 16, 2011, 10:05 AM
    shlogan
    What should I do if a main breaker is tripping, but we just replaced it a year ago?
    My main breaker trips usually when the hot water heater is running or the dryer is on. We had this problem a year ago and we replaced the main breaker. We have not had any problems after it was replaced until 3 weeks ago. I am wondering if something is making the main breaker go bad or if it is something else all together?
  • Sep 16, 2011, 11:03 AM
    Fr_Chuck
    You may want to have those specific circuits tested as well as a load test on how much power you are using, if you are using over the limits for your main, it will trip.
  • Sep 16, 2011, 12:19 PM
    tkrussell
    Too often there is a loose bolted connection in the busbar of a panel, and a breaker is changed and the problem comes back.

    Heat can migrate from the bus into the breaker and cause a nusinance trip.

    Having the load checked to be sure your not exceeding the rating of the breaker is the simplest, and wisest to do.

    Just wanted to offer another possible reason for the tripping.
  • Sep 16, 2011, 12:54 PM
    shlogan
    I appreciate the advice and will get those things checked.
  • Sep 17, 2011, 05:30 PM
    Missouri Bound
    In addition to the very good advice from TK and FR I would assk just how large is your service now? (amperage, that is)