I have a 5600 10 horse craftmen genantor the reset buttons keep plopping out with not that much of a load how can I wire it up to elemiante them
![]() |
I have a 5600 10 horse craftmen genantor the reset buttons keep plopping out with not that much of a load how can I wire it up to elemiante them
You can bypass that breaker but it is likely just doing its job. It would be downright wrong and dangerous for any of us to give directions to bypass a safety. However, give us more details and we will see if we can fix the issue. Is it this one Craftsman Briggs & Stratton Generator, Elec Start 10 HP Reviews - MySears Community
So you want to eliminate the overload safety device of the generator?? NOT a good idea.
Just replace it/them if they are tripping prematurely.
If its tripping under a light load verified with an amprobe, connections may be loose or it is bad.
Safer and Cheaper in the long run for you as mentioned.