  • Sep 12, 2011, 11:03 AM
    mikelarson
    Eliminating reset buttons
    I have a 5600 10 horse craftmen genantor the reset buttons keep plopping out with not that much of a load how can I wire it up to elemiante them
  • Sep 12, 2011, 11:48 AM
    ballengerb1
    You can bypass that breaker but it is likely just doing its job. It would be downright wrong and dangerous for any of us to give directions to bypass a safety. However, give us more details and we will see if we can fix the issue. Is it this one Craftsman Briggs & Stratton Generator, Elec Start 10 HP Reviews - MySears Community
  • Sep 12, 2011, 04:48 PM
    stanfortyman
    So you want to eliminate the overload safety device of the generator?? NOT a good idea.

    Just replace it/them if they are tripping prematurely.
  • Sep 12, 2011, 04:58 PM
    Stratmando
    If its tripping under a light load verified with an amprobe, connections may be loose or it is bad.
    Safer and Cheaper in the long run for you as mentioned.